Issue
- After creating an output point on an XPD02 attached to a BCX the output is not working.
- The CPU light of the XPD02 stays solid ON.
Environment
- XPD02
- BCX
- Expansion Modules
Cause
The expansion module was connected to the BCX while powered.
Resolution
Reload the BCX.