Microsmart Service in a Niagara R2 UNC exhibits slow or sluggish performance, impacting system responsiveness.
TAC IA Series
Niagara R2 Microsmart Service
Polling configuration is not optimized, leading to poll overruns and inefficient data refresh intervals.
  1. Maintain Recommended Poll Always Count
    • Set Poll Always count to 250 (recommended level).
  2. Adjust Cycle Time
    • Check averageExecuteTime in Poll - Status tab.
    • Increase cycleTime in Poll - Config tab to match averageExecuteTime + 1 second to prevent overruns.
  3. Optimize Minimum Poll Interval for Shadow Objects
    • Review minimumPollInterval for each Microsmart point shadow object.
    • Increase from default 1000 ms where possible.
      • Example: For space temperature shadow objects, set between 30,000 ms to 60,000 ms.
Recommended Settings
Parameter Recommended Value Notes
Poll Always Count 250 Prevents excessive polling load
Cycle Time Avg Execute Time + 1 sec Adjust based on Poll - Status tab
Minimum Poll Interval 30,000–60,000 ms (for temp) Increase from default 1,000 ms where possible