Operator precedence in PE programming
Select a Country
  • Operator precedence in PE programming
  • RandyDavis
    RandyDavis
  • AbeMeran
    AbeMeran
‎2018-09-06 10:22 AM
Last Updated: RandyDavis Champion ‎2020-03-20 10:46 AM
Care must be taken about the precedence of operators in Plain English programming to achieve expected results.
The following PE program was created with the intent of monitoring how long a point has been in alarm and unacknowledged
The user intent was to have the program increment  ‘TimeInALM’ for every minute the point has been in alarm without an ACK
WaitOneMin:
IfTS > 59 then Goto CheckALM
CheckALM:
  TimeInALM = TimeInALM + PSS\ACX2.48\Num1 Alarm1 = On and PSS\ACX2.48\Num1 AckTransToOffNorm <> 255
  IfTimeInALM > 4 thenGotoAlertGuard ElseGotoWaitOneMin
AlertGuard:
  TimeInALM = 0
  GotoWaitOneMin
Instead of incrementing as was the intent, ‘TimeInALM’ kept toggling between 0 and 1.
Andover Continuum
  • Continuum Cyberstation
  • Continuum (All CXs)
  • Continuum Plain English
The rules of precedence dictate that the + is done first then the AND. So this is what happens:
  1. We start with TimeInALM = 0
  2. PSS\ACX2.48\Num1 Alarm1 evaluates to 1 and so does PSS\ACX2.48\Num1 AckTransToOffNorm
  3. So we have
    0+1 = 1 ANDed with 1 = 1
  4. Now TimeInALM = 1, so second pass is
    1+1=2 ANDed with 1 = 0
  5. So TimeInALM is now zero and the cycle repeats
Use parentheses to enforce the order of operations.  This resolves potential ambiguities.
TimeInALM = TimeInALM + (PSS\ACX2.48\Num1 Alarm1 = On and PSS\ACX2.48\Num1 AckTransToOffNorm <> 255)
Here is the complete PE Operator Order of Precedence for reference.
Tags (3)
  • 13347
  • AbeMeran20
  • plain english