Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1927 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor.

Picard Product_Support
‎2018-09-10 02:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 10:17 PM

Issue

Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor.

Product Line

Field Devices

Environment

Fan Coil Unit installations comprising multiple Satchwell CZU Fan Coil Unit Controllers.

Stand alone discreet Satchwell CZU Mk 1, Mk2, Mk3 and Mk4 Zonemaster Controllers

CZU1201 CZU1202 CZU1203

CZU2201 CZU2202 CZU2203

CZU3201 CZU3202 CZU3203

CZU4201

Cause

From time to time the need arises for office partition layouts within a building to be revised in order to reflect changes in occupancy requirements.

This can result in the combination of numerous individual controlled spaces into a common controlled space.

This in turn may result in the need to revise associated Fan Coil Unit control systems installed in the controlled spaces affected.

Such revisions may require multiple Fan Coil Unit control systems to be controlled from a common Temperature Sensor installed in the common controlled space.

This form of control may be achieved by adopting the installation method described in the Resolution.

Should the common controlled space be of such a size as to benefit from the installation of averaging Temperature Sensors then this may be achieved by installing 4 non-adjustable Temperature Sensors. 

The 4 non-adjustable Temperature Sensors should be wired in a series-parallel configuration in order to ensure compatibility with the associated Satchwell CZU Fan Coil Unit Controller.

The series-parallel wiring configuration may be achieved by adopting the installation method described in the Resolution.

Resolution

1.  Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor. 

Multiple Satchwell CZU Fan Coil Unit Controllers should not be connected directly to a common Temperature Sensor.

Instead the common Temperature Sensor should be connected to a single Satchwell CZU Fan Coil Unit Controller.

The single Satchwell CZU Fan Coil Unit Controller should then be connected to the associated Fan Coil Unit Heating Coil Control Valve Actuators and / or Cooling Coil Control Valve Actuators.

Up to 7 Heating and / or 7 Cooling Control Valve Actuators may be wired to a single Satchwell CZU Fan Coil Unit Controller in accordance with the method shown here

2.  Averaging Temperature Sensor control.

Should the controlled space be of such a size as to benefit from the installation of averaging Temperature Sensors then 4 non-adjustable Temperature Sensors may be wired in series-parallel configuration in order to ensure connection compatibility with the associated Satchwell CZU Fan Coil Unit Controller.

The 4 non-adjustable Temperature Sensors may be wired in series-parallel configuration to a common Satchwell CZU Fan Coil Unit Controller in accordance with the method shown here

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (1)
  • Find more articles tagged with:
  • 5988
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore