Online Messages on an SLI

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Online Messages on an SLI
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1410 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Online Messages on an SLI

Picard Product_Support
‎2018-09-07 02:03 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:53 AM

Issue

Online Messages on an SLI

Environment

I/NET site

Cause

Messages coming from the Sub Lan Interface (SLI)

Resolution

A door controller (DPU) has a limited amount of memory space available for storing individual records and messages. "Resident in DPU" individual records are given priority in storage: they are never discarded. Transient (non-resident) individual records and messages are stored on a space-available basis. If a communication outage between the SLI and the door controller causes the door controller's memory capacity to be reached, older records must be discarded as new messages continue to be generated. All records are discarded on a first-in, first-out (FIFO) basis, so that the remaining records are the most recent ones.

A "DPU queue ovflw" message will also be generated to warn that data was lost. Records are discarded in the following order:

  • Transient individuals.
  • Messages.

If there are no more transient individuals to discard, routine messages will be lost. When communications between the SLI and the door controller are restored, the contents of the door controller's queue (including the "DPU queue ovflw" message) will be delivered, freeing memory in the door controller. The SLI continually requests messages from its door controllers. Retrieved messages are queued within the SLI until they can be sent to appropriate host workstation(s).

When the SLI queue is full, it will continue to accept messages from door controllers (i.e., the SLI will not cause its door controllers to discard messages). With its memory queue full, the SLI will discard older messages as newer messages are received.

This ensures that the remaining records are the most recent ones. A "DCU queue ovflw" message will be generated to warn that data was lost. When communications between the SLI and the host PC are restored, the contents of the SLI's queue (including the "DCU queue ovflw" message) will be delivered, freeing memory in the SLI.

There is also a TPA-DALL-09-0001.00 that was written on this issue.

Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 3503
  • tpa-dall-09-001.00.pdf
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore