Offline Engineering with Project Configuration Server (PCS)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Offline Engineering with Project Configuration Server (PCS)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • Benji
    Benji

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3418 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Offline Engineering with Project Configuration Server (PCS)

Picard Product_Support
‎2018-09-11 10:04 AM

Issue

A method of offline database engineering is needed for SmartStruxure. 

Product Line

EcoStruxure Building Operation

Environment

  • StruxureWare Building Operation
  • Project Configuration Server (PCS)

Cause

System integrator wants to engineering expansions and new automation to the site offline.

What is the procedure if the client already has the ES and AS devices onsite, but wants to engineer offsite?

If not can we only add one AS per project then restore / deploy just the AS and how is point referencing managed on bindings to the original site server?

Resolution

Beginning with the release 1.5 version of Project Configuration Server(PCS) is a 'deploy once' version, meaning that it allows you to make the first configuration offline. It is a full deployment meaning it may only be the ES or AS or the ES with AS connected. There are no partial deployments with bindings intact with existing servers. For deployment to include bindings between the ES and AS or other devices, they must be added to the initial deployment, which will overwrite existing configuration.

Note: the 64 AS limit is a performance issue. 64 fully loaded AS in a project takes a long time to open.

Once a server in the PCS project is deployed on site, you cannot deploy it again without manually erasing the database in the online server using the Device Administrator or uninstall and re-install the Enterprise server.

Consider the following scenario where an office wishes to use the PCS on a project with staged installation and an ES with 15 AS:

  1. Create the ES and all 15 AS in my project. You may not have the project’s communication information because none of the final IP addresses are available. So put them in with 192.168.1.x
  2. Configure all of what is needed in 5 of the AS (AS1 – AS5).
  3. Configure all of the IO and other objects in another 5 AS (AS6 – AS10)
  4. Do nothing with the last 5 AS (AS11-AS15).
  5. Create some read references in some of my programs in AS1-AS5 that are referencing objects from AS6 – AS15.
  6. Create extended trends and alarms categories at the ES.
  7. Create alarms in AS1 - AS5 that use the alarm categories.
  8. Go to the site and deploy AS 1 to AS5 (after modifying the communication parameters for those 5 so that you can bring them on line.)
    1. The alarm categories will be deployed to the AS in spite of the fact that the PCS would have had them configured as lead and shadows from the ES, which was not deployed. However, there would likely be an offline alarm generated because there was no ES and there might also be a lead/shadow alarm. The alarms will be correctly configured, however, and operational.
    2. The references to the objects from AS6 – AS15 will appear as unresolved in the AS1-AS5 reference managers.
  9. Go back to the office and finish everything needed in AS6 – AS10
  10. Create graphics at the ES referencing objects from all 15 AS.
  11. Create trend charts showing log data from all AS.
  12. Create users, domains, workspaces, etc.
  13. Go back to the site and adjust the communication parameters for all the remaining 10 AS and for the ES
  14. Deploy AS6 - AS10 and the ES.
    1. Initially, the AS1-AS5 have empty/wrong communication settings to the ES. It requires a manual “Repair Com-settings” from the user logged on to ES (at the site). When the Com-settings are ok, then the bindings from AS1- AS5 to AS6-AS10 will be resolved after a few minutes.
    2. When the Communication settings in AS1-AS5 for the ES are correct, the synchronization for lead/shadow relationships starts updating the alarm categories that we discussed in step 8a.
    3. The graphics in the ES will have resolved bindings for objects from AS1 – AS10, but unresolved bindings from AS11-AS15. In fact, they will be resolved to AS1-AS5 even if you haven't corrected the Com-settings in AS1-AS5. The ES knows all the AS.
  15. Go back to the office and finish up my work on AS11-AS15. Part of this process is the creation of programs that reference objects in AS1 – AS10.
  16. Go to the site and deploy AS11 – AS15.
    1. All of the read references to objects from AS1 – AS10 will automatically fix up once the Com-settings for the ES in AS11-AS15 are correct. It might, however,  take a few minutes.
    2. All of the references in the ES graphics for AS will be operational.

 

Further information can be found on Building Operation WebHelp.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 16571
  • projects
  • upload
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore