Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Offline Database Edit

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Offline Database Edit
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1503 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Offline Database Edit

Picard Product_Support
‎2018-09-06 03:11 PM

Issue

Offline Database Edit

Environment

I/NET Seven

Cause

This facility lets you modify controller databases without having to connect to the actual controller.

Resolution

In I/NET, there is a feature called Offline Database Edit that allows the user to create, or modify new and existing DCUXXXX.SAV files. In order to get to this editor, the user needs to follow these steps:

  1. I/NET displays this dialog when you select Connect while the System Work Offline option is selected from the System drop down list. This dialog allows you to select the DCUXXXX .SAV file you wish to edit from among a list of those available. This dialog displays the Link address, station address, controller type, station name, number of stations, save date and filename. Additionally, you may Add, Delete, and/or Copy your files.

Note: Before attempting to perform offline edits of your database, you should ensure that the latest version of the DCUXXXX.SAV file is present on the client from which you will be performing the edits. To get the latest DCUXXXX.SAV file, connect to the controller and perform a Station Save.

If you elect to work offline after a connection has been made, your connection will be terminated automatically and you must reconnect before you can resume working in online mode.

Note: All graphic pages will be closed when this option is selected.

Connecting to an Offline Controller

  1. Highlight the SAV file you wish to edit and press OK. The status bar at the bottom of the main I/NET window shows the name of the selected SAV file, the controller type, and an indication that you are working offline. Select Edit from the I/NET main menu and choose either Host Computer or Controller. You may then select the editor you wish to modify using the sub-menus presented in the same way you would when operating in the online mode.
     

Once you have finished modifying your DCUXXXX.SAV files, perform a Station Restore to have the changes applied globally.

Options

The following options are available from within the Connect Offline dialog:

  1. Add – Use this option to create a new SAV file. When you select Add, the system displays the Offline Add dialog. This option is useful for preparing your system to use a controller that has not yet been installed. Later, when the controller is connected, you can simply perform a Station Restore to download the SAV file to the device.
  2. Delete – Use this option to delete a SAV file from the system. You will be prompted to confirm the Delete request.
  3. Copy – Use this option to copy an existing SAV file. When you select Copy, the system displays the Offline Copy dialog. The new save file will retain the various editor parameter settings that were stored in the original SAV file. This can help to reduce the amount of configuring you'll have to perform on the new SAV file.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1787
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore