Objects don't work properly or indicate fault when created in a b3 controller.
  • Objects don't work properly or indicate fault when created in a b3 controller.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 02:08 PM
Go to templates folder
Drag Event Enrollment to controller to create a new event enrollment
It prompts for event notification and point reference and enrollment looks fine.
When alarm is tested the event notification does not work and indicates fault.
Continuum
BCX40xx
B3
B4920
A Send to Database was not performed on the controller in the BACnet side of the Continuum Object Tree.
When objects are added or modified on the Infinity side of Continuum's Object Tree, the changes do not take affect in the controller until a Send to Database is performed on the controller from the BACnet portion of Continuum Explorer Object Tree.
  • 4591