'Object attribute not available' when assigning 3rd party bacnet object to a numeric
  • 'Object attribute not available' when assigning 3rd party bacnet object to a numeric
  • Alan_Wood
    Alan_Wood
‎2018-09-06 01:08 PM
Mapping a 3rd party bacnet point to a numeric gives 'object attribute not available'
Continuum
BCX
Viconics Stat
The path to the object couldn't be found
Deleted the bacnet network
Deleted the BCX
Find new bacnet
Able to map the 3rd party object to the numeric using ReadProperty with no error
Note: Mapping a 2nd Viconic stat to the original BCX gave the same error, but mapping either stat to another BCX on the same subnet worked without error prior to the delete/Find.