Numeric Public error Unsupported feature in b3 script program
  • Numeric Public error Unsupported feature in b3 script program
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • SangKim
    SangKim
‎2018-09-06 09:41 AM
Last Updated: Sisko DavidChild Sisko ‎2020-02-24 07:07 AM
In declaring a variable, the binding qualifier PUBLIC in a BACnet b3 controller's script program such as "Numeric Public numPoint" gives the error "Unsupported feature" when saving script program.
  • AS
  • BACnet b3 i2 Infinet controller
  • Script
  • Numeric Public
Need Numeric variable to be readable and writable in BACnet b3 or Infinet i2 controller script programming.
The Public qualifier is supported in SmartX servers (AS, ASP, ASB) and SmartX IP controller script program only.
For BACnet b3 or infinet i2 controller script programming, use Input and Output qualifier and bind to the same object's property outside the program.
Tags (3)
  • 15680
  • DavidShore20
  • declaration