Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Not possible to bind Function Block to RelinquishDefault of a BACnet Multistate value in an SE8000 controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Not possible to bind Function Block to RelinquishDefault of a BACnet Multistate value in an SE8000 controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3158 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Not possible to bind Function Block to RelinquishDefault of a BACnet Multistate value in an SE8000 controller

Picard Product_Support
‎2018-09-11 11:28 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:06 AM

Issue

It is not possible to bind a point in a Function Block program to the RelinquishDefault property of a BACnet Multistate value in an SE8000 controller.

Product Line

EcoStruxure Building Operation

Environment

  • StruxureWare Building Operation(SBO) 1.6.1
  • SE-8000 series Room Controller

Cause

In some circumstances the user may wish to change the value from both the HMI in SE8000 and from a Function block program in SBO, and in this case the RelinquishDefault property must be used.

Resolution

A possible workaround is to use a LUA script in the SE8000 controller.

Idea 1:

  • Write a LUA script that will check if the Priority array (ex. priority 16) value has changed for the list of points that the user wants to modify.
  • If there is an entry in the Priority array, have the LUA script copy that value to Relinquish_default, then relinquish the corresponding priority array entry.

Idea 2:

  • There are 6 LUA "scratchpad" BACnet AVs that the user can write too.
  • When the LUA script sees a change in those AVs, it can copy the value to a specific AV's relinquish default.
  • For example, scratchpad AV25 can be used to "shadow" a setpoint. So when AV25 changes, the LUA script will copy the present value of AV25 into the Relinquish_default of whatever the Setpoint's AV is.

Example of the LUA script in the SE8000 controller for the above:
If value AV25 is bigger than 0, the value of AV25 is written on AV39 Relinquish_default property (priority17) and then AV25 is set to 0.

if ME.AV25 > 0 then ME.AV39_Present_Value[17] = (ME.AV25/10); end ME.AV25 = 0

LUA programming guide for SE8000 Room controllers

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (1)
  • Find more articles tagged with:
  • 17948
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore