Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

No events in the Report Server SQL database and events not updating

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • No events in the Report Server SQL database and events not updating
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3110 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

No events in the Report Server SQL database and events not updating

Product_Support
‎2018-09-11 01:06 PM

Last Updated: ContentModerator Explorer ‎2025-09-01 03:36 AM

Issue

No events are transferred to the Report Server SQL database. Trend logs are transferred just fine.

In the report agent log you can see this message "Sequence contains no elements"

Product Line

EcoStruxure Building Operation

Environment

Report Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

The Enterprise Server has been renamed before the Report Server has been installed or before the Report Server Agent has started collecting data.

Resolution

This issue will be fixed in a future version, but until that, do the following to correct the issue:

The fix is split into two sections. First, a section working with the "event.db" file from the SBO database, and second a section working with the "StruxureWareReportsDB" from SQL Management Studio.


"event.db" from the SBO database

  1. Download http://www.sqliteexpert.com/download.html (Just take the personal one)
  2. Stop the Enterprise Server
  3. Copy the "event.db" file to a safe location
  4. Attach the "event.db" file to "SQLite Expert Studio"
  5. Get the first event from the event.db using the following query in the "SQL" tab:
    SELECT SEQNO,TimeStamp,EventGUID,SourceServer
    FROM t_7E_2FSystem_2FEvents_2FEventLog_2FEventRecords
    ORDER BY SeqNo
    LIMIT 1;

  6. Convert the TimeStamp with this "SBO TimeStamp Converter" tool

"StruxureWareReportsDB" using SQL Management Studio

  1. Write the following SQL query in SQL Management Studio, using the converted time stamp, and the Guid you found previously.
    INSERT INTO StruxureWareReportsDB.dbo.tbEvents
    (DateTimeStamp,SeqNo,OriginalSeqNo,Guid) VALUES 
    ('2014-04-17 08:35:23.857','1','1', '380d1c4c-c60b-11e3-8ecb-b8ac6f81243c')
  2. Start the Enterprise Server again
  3. Restart the Report Agent and let it run for a while.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
SBO TimeStamp Converter.zip
Tags (5)
  • Find more articles tagged with:
  • 17527
  • 26975
  • defect
  • RobertAndriolo19
  • RobertAndriolo21
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore