Niagara R2 UNC Time Inaccuracy – Error Loading timezones.txt
  • Niagara R2 UNC Time Inaccuracy – Error Loading timezones.txt
  • CraigEl
    CraigEl
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 10:34 AM
Last Updated: Administrator CraigEl Administrator ‎2025-12-04 11:20 PM
A Niagara R2 UNC does not keep time accurately. The time does not simply drift by seconds; it jumps by hours. Attempts to change the time using the Admin Tool fail. On startup, the Standard Output Window displays:
ERROR: Cannot load /tffs/rel//nre/lib/timezones.txt
java.lang.NumberFormatException
TAC IA Series
Niagara R2 UNC
The timezones.txt file on the UNC is corrupt, preventing proper time synchronization.
Replace the corrupt timezones.txt file with a valid copy from a functional UNC:
  1. Access the file via the Admin Tool dropdown menu.
  2. Copy the contents of timezones.txt from a working UNC.
  3. Paste the contents into the problem UNC.
  4. Restart the station to confirm accurate timekeeping.
  • TAC IA Series
Tags (2)
  • 12755
  • CraigEllis25