Issue
A Niagara R2 UNC station fails to start and displays the following error in the Standard Output Window:
FATAL: cannot boot station from sns
java.lang.ClassNotFoundException: tridiumx.vlon.VlonService
Product Line
TAC IA SeriesEnvironment
Niagara R2
Cause
Resolution
-
Install the Vlon Module into the UNC
- Use Admin Tool to connect to the UNC.
- Navigate to the Installation tab and click Installation Wizard.
- In the Select Distribution Directory dialog, highlight emb and click Install.
- In the Niagara Remote Installation dialog, select Configure Modules Only and click Next.
- In the Configure Modules dialog, select the Vlon module by checking the Upgrade/Add column.
- Click Next when finished.
- On the Database Backup dialog, leave the red check mark next to the station database name and click Next.
- Enter the station username and password when prompted.
- In the Niagara License dialog, click Finish.
-
Restart the UNC after installation is complete.