Niagara R2 UNC Station Fails to Start – Missing Module Dependencies
  • Niagara R2 UNC Station Fails to Start – Missing Module Dependencies
  • CraigEl
    CraigEl
  • SESA113595
    SESA113595
‎2018-09-06 01:09 PM
Last Updated: Administrator CraigEl Administrator ‎2025-12-11 04:12 PM
A station will not start in an I/A Series R2 (Niagara) UNC. The output window shows errors similar to:
Invalid jar: /tffs/modules/coreRuntime-2.301.522.v2.jar
WARNING: Module alm 2.301.522.v1 [...] Missing dependency: coreRuntime-2.301
WARNING: Module lonworks 2.301.522.v1 [...] Missing dependency: coreRuntime-2.301
FATAL: Could not load class "tridium.tools.StationMain".
TAC IA Series
I/A Series R2 UNC
The station cannot start because required module dependencies (e.g., coreRuntime) are missing or corrupted. This typically occurs after an incomplete upgrade or module mismatch.
Perform a full install (upgrade) of the UNC, including:
  1. Upgrade the Operating System, NRE, and niagarad.
  2. On the Configure Modules screen:
    • Check Upgrade/Add for all modules shown as installed.>p>
    • This forces all modules to reload and resolve dependency issues.
  3. Restart the station and verify successful startup.
  • TAC IA Series
Tags (2)
  • 6572
  • CraigEllis25