Issue
A Niagara R2 UNC station fails to start and displays the following error in the Standard Output Window:
FATAL: Cannot boot station from sns
java.lang.IllegalStateException: NodeProperty.readExternal:
tridium.foundation.TRuntimeException E_INVALID_DSTABLE_CODE {165.16}
Product Line
TAC IA SeriesEnvironment
- Niagara R2 UNC-410
- Niagara R2 UNC-520
Cause
lonTrane module was not installed, causing the station to fail during boot.Resolution
- Review the Standard Output Window error messages for references to missing jar files.
- Identify which Lon devices are configured in the station.
- Install all required Lon modules (jar files) on the UNC.
- Example: If Trane Lon devices are present, ensure the
lonTranemodule is installed.
- Example: If Trane Lon devices are present, ensure the
- Restart the UNC station after installing the missing modules.