Issue
When attempting to start a Niagara R2 station, the following error appears in the Standard Output Window:
ERROR: Reading Ecdis210 [1371] Ecdis210 Subnet = 1 Node = 2 state = config_online
FATAL: Cannot boot station from sns java.io.UTFDataFormatException
Product Line
TAC IA SeriesEnvironment
- Niagara R2 UNC-410
- Niagara R2 UNC-520
Cause
Resolution
-
Verify Module Installation
Ensure the correct Distech module is installed for the station. -
Restore from Backup
If the module is correct and the error persists, the station database is corrupted.- Replace the corrupted database with a valid backup copy.
- Restart the station after restoring the backup.