Niagara R2 Modbus RTU Integration with Eaton Series 2000 Xpert Power Meter
  • Niagara R2 Modbus RTU Integration with Eaton Series 2000 Xpert Power Meter
  • CraigEl
    CraigEl
  • SESA113595
    SESA113595
‎2018-09-06 10:53 AM
Last Updated: Administrator CraigEl Administrator ‎2025-12-07 04:16 PM
Difficulty integrating Eaton Series 2000 Xpert Power Meter with Niagara R2 using Modbus RTU due to unclear documentation on register map differences between IP and RTU protocols.
TAC IA Series
  • I/A Series UNC
  • Eaton Series 2000 Xpert Power Meter
The Eaton documentation does not clearly differentiate between Modbus register maps for TCP/IP and RS-485 RTU, leading to confusion during integration.
  1. Locate RS-485 Map:
    The Modbus RTU RS-485 register map is found under Eaton IQ-250/260 meter documentation, not under Series 2000.
  2. Access Embedded Utility:
    Use the embedded setup and monitoring software on the Eaton Power Meter.
    • Click the Help button to upload the Modbus map as an Excel spreadsheet.
    • Note: This map represents the TCP/IP Modbus register map, not RS-485.
  3. Connection Details:
    • Access via a standard internet browser using Ethernet cable.
    • Default IP address: 192.168.1.1.
  4. Register Calculation:
    Convert Eaton’s decimal register number to standard 5-digit Modbus register by adding 40000.
    • Example: Register #1000 → 40000 + 1000 = 41000 (Volts Phase A - Neutral).
  • TAC IA Series