Niagara R2 Modbus Driver Support for 6-Digit Address Format
  • Niagara R2 Modbus Driver Support for 6-Digit Address Format
  • CraigEl
    CraigEl
‎2018-09-06 02:28 PM
Last Updated: Administrator CraigEl Administrator ‎2025-12-14 05:51 PM
Does the Niagara R2 Modbus driver support a 6-digit address format?
TAC IA Series
The Modbus protocol uses different notations for register addressing. The 6-digit format (e.g., 400001–409999) is a convention that shifts the type digit one position to the left to represent more registers. Niagara R2 does not support this convention when using Modbus-formatted addresses.
  • The 6-digit Modbus notation is not supported in Niagara R2 when using Modbus format in the driver.
  • However, you can use decimal or hexadecimal notation to specify addresses beyond the 5-digit range.
  • When using Modbus format:
    • The leftmost digit (e.g., '4' for holding registers) indicates the point type.
    • The driver subtracts 1 from the entered address because Modbus uses base-1 indexing, while decimal uses base-0.
Example Conversion
To read data from register 422202:
  1. Drop the leading digit → 22202
  2. Subtract 1 → Decimal address 22201
  3. Optionally convert to hex → 56B9
Key Notes:
  • First 1,000 holding registers:
    • Modbus notation: 40001–49999
    • Decimal: 0–9998
    • Hex: 0–270E
  • There are 64,000 holding registers available, but Modbus format limits notation to 5 digits.
  • TAC IA Series
Tags (3)
  • 3894
  • CraigEllis23
  • CraigEllis25
0% helpful (0/1)