Issue
In Niagara R2, master-slave schedules are not working. The slave schedule goes into fault and will not clear. The following error appears in the UNC standard output window:
ERROR: Could not init node [/OZS_UNC1/IbsAsdNetwork/AHU_9/MZ2_93/Schedule_8]
Product Line
TAC IA SeriesEnvironment
Niagara R2
Cause
This fault occurs when:
- The Enterprise Server has a holiday calendar and master schedule.
- The UNC only has a slave schedule.
- After a UNC reboot, the slave schedule checks the master schedule on the server to determine if it’s a holiday.
- If there is a communication issue during this check, the slave schedule object enters fault.
Resolution
- Delete and re-create the slave schedule object in the UNC.
- Ensure both master/slave schedule and master/slave calendar objects exist in both the Enterprise Server and UNC stations.
- Verify communication between the UNC and Enterprise Server before rebooting.