Niagara R2 Master Enterprise Server – Features and Poll Archive Configuration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara R2 Master Enterprise Server – Features and Poll Archive Configuration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa119747
    sesa119747
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1234 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara R2 Master Enterprise Server – Features and Poll Archive Configuration

Picard Product_Support
‎2018-09-06 02:34 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-14 08:44 PM

Issue

Understanding how a Niagara R2 Master Enterprise Server operates and its role in archiving data from subordinate Enterprise Servers.

Product Line

TAC IA Series

Environment

Niagara R2 Master Enterprise Server

Cause

The installation uses a Master Enterprise Server and requires details on its functionality, especially for log archiving and multisite polling.

Resolution

Key features and configuration steps for Niagara R2 Master Enterprise Server:

  1. License Requirement

    • Must include the “multisite” feature to enable Poll Archive Service.
  2. Poll Archive Service

    • Located in tridiumx / Multisite.jar.
    • Collects data from the Application Database (App folder) of subordinate servers.
    • Appends new polled data to existing archives.
  3. Address Book Setup

    • Include all subordinate stations as clients in the Master Enterprise Server’s Address Book.
  4. Poll Groups

    • Enable Poll Archive Groups individually.
    • Configure poll frequency (hours) in Poll Archive Service properties.
    • Optional: Use Date-Time Trigger for scheduled polling via “Link From, Link To”.
  5. Manual Polling

    • Navigate to Services Container → Go → Service Manager → Poll Archive Service.
    • Select Poll Group and click Invoke.
  6. Log Data Sources

    • Direct polling from log objects in UNC 5x0/6x0:
      • Enable “polled” in archiveSetup.
    • If polling archived data:
      • Client station log service = Archive Local.
    • If polling live log objects:
      • Client station log service = Archive Remote.
  7. Viewing Archived Data

    • Use WorkPlace Pro Database Browser or web servlets:
      • appdb, archive/index, or chart/log.
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 3596
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore