New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Niagara R2 LON and Serial Tunnel Client Port Configuration
Building Automation Knowledge Base
Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
What port is used for the Niagara R2 LON and Serial tunnel clients?
Product Line
TAC IA Series
Environment
Niagara R2
Cause
Network configuration changes require port forwarding for tunneling. The correct port must be identified to allow communication through routers and firewalls.
Resolution
The LON and Serial tunnel clients use the same port as the UNC station.
Default port: 80
If the station port is modified, the tunnel clients will use the updated port number.