Issue
Product Line
TAC IA SeriesEnvironment
Niagara R2 Enterprise Server
Cause
Resolution
- There is no recommended maximum point count or trend interval for Niagara R2 Enterprise Server.
- Trend samples are stored in the app database located at:
C:\niagara\stations\app - When this folder becomes too large, the Enterprise Server performance will be affected.
- Workaround:
- Periodically move or purge the contents of the
appfolder to maintain optimal performance. - Implement a regular maintenance schedule to prevent excessive database growth.
- Periodically move or purge the contents of the
Best Practices for Trend Configuration
-
Set Appropriate Sampling Intervals
- Avoid very short intervals (e.g., <1 minute) unless absolutely necessary.
- Use intervals that align with operational needs (e.g., 5–15 minutes for HVAC points).
-
Limit Retention Periods
- Configure trend logs to purge older data automatically after a defined period (e.g., 30–90 days).
- Export historical data to external storage if long-term archiving is required.
-
Use Averaging or Summarization
- For high-frequency data, consider logging averages or summaries instead of raw samples to reduce database size.
-
Monitor Database Growth
- Regularly check the size of the
appfolder and set alerts for excessive growth.
- Regularly check the size of the