Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Niagara R2 Enterprise Server – Clearing Alarm History and Alarm File to Improve Station Performance

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara R2 Enterprise Server – Clearing Alarm History and Alarm File to Improve Station Performance
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2131 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara R2 Enterprise Server – Clearing Alarm History and Alarm File to Improve Station Performance

Picard Product_Support
‎2018-09-06 02:57 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-01 10:16 PM

Issue

Niagara R2 Enterprise Server stations may experience slow startup or performance issues due to excessive historical alarms stored in the database. Users need methods to remove alarm history or the alarm file to restore normal operation.

Product Line

TAC IA Series

Environment

Niagara R2 Enterprise Server

Cause

Accumulation of alarms and logged data in the station’s database increases boot time and impacts performance. The alarm archive file and associated historical data can grow significantly over time.

Resolution

There are two main approaches to clear alarms and logged data:


Method 1: Delete the APP Folder (Complete Removal)

This method removes all archived data, including alarms, logs, and events.
Steps:

  1. Stop the Niagara Service:
    • Open Control Panel → Administrative Tools → Services.
    • Locate Niagara, right-click, and select Stop.
  2. Delete the APP Folder:
    • Navigate to:
      C:\Niagara\stations\[station name]\app
      
    • Delete the app folder.
  3. Restart the Niagara Service:
    • Return to Services, right-click Niagara, and select Start.

Result: The station will recreate the APP folder and Cloudscape structure on restart. All archived data, including alarms, will be cleared.


Method 2: Use SQL Queries via appdb/queryForm Servlet (Selective Removal)

This method allows targeted deletion of alarm history without removing all logged data.
Steps:

  1. Open a browser and navigate to:
    http://[ipaddress]/appdb/queryForm
    
  2. Enter and execute the SQL query:
    delete from event.eventhistory
    
  3. Repeat for other tables if needed (refer to SQL_Tutorial\QueryExamples_10_6_04.pdf for examples).

Note: This process may take time depending on database size.

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 2663
  • CraigEllis25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore