Issue
In a Niagara R2/DMS integration, the re-learn of the DMS database fails after some points were deleted in the DMS system.
Product Line
TAC IA SeriesEnvironment
- Niagara R2 (all versions)
- DMS (all versions)
Cause
The DMS driver uses the LOGPT index (1–250) to scan points during the learn process. When points are missing, the DMS panel returns “NOPOINT.” If multiple consecutive “NOPOINT” responses occur, the learn process terminates early. This happens when points have been deleted or re-created, causing gaps in LOGPT assignments.
Resolution
Adjust the learnNoPointAbortCount property in the DMS driver:
- Set
learnNoPointAbortCountto 250 to ensure all possible points are scanned, even if gaps exist. - Note: This will increase the time required for the learn process but guarantees a complete scan.
Additional Notes:
- If the DMS database was reloaded from a saved backup, points will have consecutive
LOGPTnumbers, and gaps will not occur. - Use this setting only when gaps are expected due to point deletion or creation.