Issue
Product Line
TAC IA SeriesEnvironment
- Niagara R2 UNC
- Niagara G3 ENS
Cause
Resolution
This integration is possible by configuring the BACnetRecipient object in Niagara R2.
Follow these steps:
- Refer to the “Configuring for BACnet Alarm Generation” section in the R2 BACnet Integration Reference Guide.
- Add the G3 station as a BACnet device under the R2 BACnetService.
- Add the R2 UNCs as BACnet devices under the G3 NiagaraNetwork.
Tip: The most common oversight is failing to add the G3 station as a BACnet device in R2.