New graphic opens in a very small pane at the edge of the screen

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • New graphic opens in a very small pane at the edge of the screen
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • RobertAndriolo
    RobertAndriolo
  • David_Kendrick
    David_Kendrick
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1917 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

New graphic opens in a very small pane at the edge of the screen

Admiral David_Kendrick Admiral
‎2019-01-17 03:02 AM

Last Updated: Picard RobertAndriolo Picard ‎2019-05-30 05:17 AM

Issue

Most systems have an Overview Graphic of the whole building.  The user then navigates from this graphic to specific floors and rooms of interest.

If the Workspace is configured incorrectly, navigating to a newly selected graphic does not work as expected.

The overview graphic does not disappear and the new graphic is forced to open very small at the edge of the screen.

Product Line

Building Operation Enterprise Server

Environment

Workspaces

Cause

The standard Administration and Engineering Workspaces used in EBO contain a Work Area Window (WAW) which is necessary 'space' to show a selected graphic/trend/schedule

If an Overview Graphic Pane is created in a Customer Workspace and this graphic takes up most of the screen, there is no space left to show the new object which the customer wishes to see

Note: The Overview Graphic 'Building' is now shown in a Graphic Viewer only

 WAW3.png

When the system tries to open a new graphic, there is not space to open it in, The graphic is forced to open at the very edge of the screen and is therefore very small.

WAW4.png

Resolution

General information about creating and using Graphic Panes, Work Area Windows and Panel Components can be found in the EBO webhelp, But for specific information on how to prevent a graphic opening at the edge of the screen see below. 

Rather than adding a Graphic Pane to the Workspace to show the Overview Graphic add a Work Area Window (WAW) instead.

WAW6.png

Next, define the required Overview graphic as the initial path for the WAW on startup so the Overview graphic opens at user log on.


WAW7.png

Note: The Overview graphic 'Building' is now shown in the WAW rather than the Graphic Viewer.

WAW8.png

Graphics will always close themselves on navigation to the next object by default when used with a WAW (this can be changed).

As soon as the user needs to navigate away from the overview page to a new graphic/schedule/trend, the system can use the WAW which will then use most of the screen as the 'space' to show it.

In this case, as soon as the link to the next graphic 'Floor' is pressed, the first graphic 'Building' closes according to its default and the new object is shown in its place.

WAW9.png

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidKendrick19
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore