New SCU 1284 out of the box shows up with an * in Netcon during setup

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • New SCU 1284 out of the box shows up with an * in Netcon during setup
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • Chris_Asbury
    Chris_Asbury
  • Roger_Bently
    Roger_Bently

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1145 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

New SCU 1284 out of the box shows up with an * in Netcon during setup

Picard Product_Support
‎2018-09-07 03:12 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 06:16 PM

Issue

A modem is already connected to a remote site's tap. Settings in the modem need to be changed. Can this be done by dialing into the modem in its present configuration?

Product Line

TAC INET

Environment

I/NET remote site communicating via dialup modem

Cause

The remote site's modem needs to be connected to a PC or Laptop.

Resolution

No, a modem can not be configured by using its present configurations. Windows HyperTerminal is suggested to edit modem settings. 

Refer to TCON 226 (Dial Applications) and TCON 101 (Taps and Repeaters). For emulated tap set up, refer to the appropriate Controller TCON.

Issue

A new SCU 1284 out of the box that you are setting up and it shows up with an * in Netcon.

Product Line

TAC INET

Environment

  • SCU 1284
  • Netcon

Cause

SCU's manufactured before 2009:  There is really nothing wrong with the SCU itself, but there may be an Eprom on the board that is not the correct one. It is the one that is used for the SCU 1280.

Newer SCU's: This is generally caused by an incorrect setting in the MCU configuration

Resolution

Verify that you have the correct MCU configuration settings.  An SCU 1284 should be set to DPU.  An SCU 1280 or 1200 should be set to DIO.  Check Network configuration to see if the issue has cleared up.

If it has not cleared up try the following:

  • Delete the item from Network Configuration and allow it to repopulate.
  • Ensure that the DIP switch is set to the correct address.
  • Follow the instructions to reset the SCU located in Reset Instructions for 1200 Series SCU.  Then reload the bin file.

If you are still having issues then the best option is to send that unit back and have it replaced with another.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 3097
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of