NetController IO Bus Comm parameters.
  • NetController IO Bus Comm parameters.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 09:21 AM
What is baud rate of the Netcontroller IO Bus?
  • NetController
  • IO Bus
  • ACC Lon
  • FTT-10A
        Parameter      ACC LON       FTT-10A
  • Baud Rate    39,063            78,125
  • Duplex         Half                 Half
  • Data Bits      8                    8
  • Stop Bits      1                    1
  • Parity           None               None
The ACC LON data signal is Differential Manchester Encoded.  The packets therefore cannot be viewed with a generic sniffer like a UART based comm signal.
  • 16967