NV Not working between Xenta controller and Xenta 913 server
  • NV Not working between Xenta controller and Xenta 913 server
  • PeterLarsen
    PeterLarsen
‎2018-09-06 11:06 AM
The NV in my Xenta 401 is not updating the value defined in a Xenta 913
Vista 5.xx
Network variable is only setup to work between Xenta controller.
The network variable will not work between a Xenta 913 and a Xenta programmable controller
The best solution is to insert the LNS or classic network into the Xenta 913 then use a connection object in the Xenta 913 to transfer the value
  • 11204