Issue
There is only 1 input available, but the end-user wants more than 1 sensor to be connected, where the reading will be averaged.
Product Line
EcoStruxure Building Operation, EcoStruxure Building Expert
Environment
- Building Operation Workstation
- Building Operation Automation Server
- SSL SE8000
Cause
The wrong sensor type or incorrect wiring might have been used.
Resolution
4 resistive sensors of the same type are required.
Depending on scenario, 2 sensors may have to be fitted adjacent to each other, or fit 2 sensors into 1 sensor housing to achieve the correct number of zones to be monitored.
For wiring follow the drawing below: