Monitoring a Controller's online or offline Status

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Monitoring a Controller's online or offline Status
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2084 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Monitoring a Controller's online or offline Status

Picard Product_Support
‎2018-09-06 01:41 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-01 08:27 AM

Issue

Needing to monitor a controller's online or offline status. I/NET AMT will generate a station lost alarm when a controller is offline, however it is sometimes desired to have a point that can be monitored to alarm as well.

Product Line

TAC INET

Environment

  • subLAN
  • Controller Lan; C-LAN
  • Xenta 527

Cause

I/NET AMT will generate a Station lost alarm when a controller is offline, however it is sometime desired to have a point that can be monitored to alarm as well.

Resolution

Monitoring SubLAN Controllers

  1. Connect to the Sub Lan Interface Controller (7798, 7793)
  2. Create an internal DA point called LLSSPP_Offline, with LLSSPP being the address of the subLAN device
  3. Add a Calculation to the point LLSSPP_Offline
  4. Enter this Calculation: OLD(P0)
  5. Set P0 to equal any External input point the subLAN device LLSSPP
  6. Click okay
  7. The result of this calculation is that the point will equal 1 whenever the referenced point goes old

Monitoring Controller LAN or C-LAN devices

  1. Connect the Controller you wish to monitor
  2. Change an external point's Global Level to "Link" (If a point already is set to system, use it.)
  3. Connect to a second Controller on the same physical C-LAN (for best results use one physically closer to the NPR or Tap)
  4. Create an indirect point referencing the point created in step 2
  5. Create an internal DA point called LLSS_Offline, with LLSS being the address of the controller
  6. Add a Calculation to the LLSS_Offline point
  7. Enter this Calculation: OLD(P0)
  8. Set P0 to equal the indirect point created in step 4
  9. Click OK
  10. The result of this calculation is that the point will equal 1 whenever the indirect point goes old, which should only occur when the controller is offline. 

Monitoring NPR or Xenta 527 devices

  1. Connect to a Controller under the device you wish to monitor
  2. Change an external point's Global Level to "system" (Use an existing global point if available)
  3. Connect to a second Controller under the device you wish to monitor
  4. Change an external point's Global Level to "system" (Use an existing global point if available)
  5. Connect to a controller underneath a different NPR or 527 
  6. Create an internal DA point called Link _LL_Offline, with LL being the Link address of the 527 or NPR being monitored
  7. Create 2 indirect points referencing the global points created in steps 2 and 4
  8. Add a Calculation to the Link _LL_Offline point
  9. Enter this Calculation: OLD(P0)&OLD(P1)
  10. Set P0 and P1 to equal the indirect points created in step 7
  11. Click okay
  12. The result of this calculation is that the DA point will equal 1 whenever both of the referenced indirect points go old.  This should only happen when communication is interrupted to both controllers indicating the most likely cause is the NPR being offline. Please be aware of other potential causes of 2 controllers on the same link going offline. Examples include power circuit failure or cut wire when selecting which controllers to monitor. 
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5433
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of