Modbus integration to Data Industrial Series 3050 BTU monitor

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Modbus integration to Data Industrial Series 3050 BTU monitor
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1551 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Modbus integration to Data Industrial Series 3050 BTU monitor

Picard Product_Support
‎2018-09-06 03:14 PM

Issue

Modbus integration to Data Industrial Series 3050 BTU monitor

Environment

I/A Series G3 ENC-520 Modbus Asynchronous (Async) driver

Cause

Required to read the values in the BTU monitor via Modbus Async.

Resolution

The below Modbus registers table is provided by the BTU monitor manufacturer.

Here are the basic procedures and settings in an ENC for this integration.

  1. Add a ModbusAsyncNetwork to the station database.
     
  2. In the ModbusAsyncNetwork properties, configure the Serial Port Config.
    Port Name: COMX (where X is the COM port number of the ENC used for this integration).
    Baud Rate: As per baud rate setting in the Modbus device. We recommend the baud rate of 9600 as this appears to work best with this device.
    Data Bits: 8
    Stop Bits: 1
    Parity: None
    Flow Control Mode: No
     
  3. Other properties of the ModbusAsyncNetwork to be left at its default values.
     
  4. Add a new Modbus Async Device to the ModbusAsyncNetwork. The device address is as per address set in the BTU monitor device.
     
  5. Leave all properties in the Modbus Async Device object as their default values.
     
  6. Go to the Points folder of the Modbus Async Device and add the required Modbus objects. Configure the properties of each object as per the following.
    Address Format: Decimal
    Address: Refer to the table above. If reading register 30002, use 2 as the address.
    Reg Type: Input
    Data Type: Long
     
  7. Set the Facets for the object
     
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 8246
  • data-industrial
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of