Modbus communication return the wrong value or result in error code.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Modbus communication return the wrong value or result in error code.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterLarsen
    PeterLarsen
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4056 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Modbus communication return the wrong value or result in error code.

Picard Product_Support
‎2018-09-06 02:24 PM

Last Updated: Spock PeterLarsen Spock ‎2022-08-30 02:41 AM

Issue

Modbus slaves are programmed according to device documentation, but either the wrong values are returned or error codes complaining about invalid address.

Product Line

TAC Vista

Environment

  • Xenta 913
  • Xenta 731
  • Xenta 511:B

Cause

The XBuilder Device Editor has two ways to address modbus registers. The improper usage of these methods can cause communication problems because the wrong register is polled.

1. Fixed Address Blocks

This method combines the function code and register address to produce a single number format that serves multiple function codes. This is sometimes referred to as numerical notation.

A poll of a holding register uses function 03 and an address from 00 00 to FF FF. When using Fixed Address Blocks a message of function code 03 and address 00 00 is displayed as 40001. Due to this combination it is limited to 9,999 addresses per function code.

Type Function Code  Address
 Coil Status  01  00001-9999
 Input Status  02  10001-19999
 Holding Register  03  40001-49999
 Input Register  04  30001-39999

When the device editor is using Fixed Address Blocks then the numerical number is parsed from the Register in the following way.

Register Function Code Address
1-9999 01 Register - 1
10001-19999 02 Register - 10001
30001-39999 04 Register - 30001
40001-49999 03 Register - 40001

2. Function Code Tables

(Discrete Input, Coil, Input Register, Holding Register)

This addressing format is closer to the actual protocol and keeps the function code separate from the register address. It also provides full use of the addresses from 0 to 65535.

Table Function Code
Discrete Input 02
Coil 01
Input Register 04
Holding Register 03

 


If the wrong format is used it can result in failure to communicate because the wrong register is used. For example polling register address 40010 on function code 03 when it should have been address 9 on function code 03.

Resolution

The documentation of the product being interfaced with is the best guide on the register addressing and the format they use.

If the documentation does not directly specify the information then use the follow hints to guide your selection:

Hints to use Function Code Tables

  1. Addresses that fall on zero (0, 10000, 30000, or 40001)
  2. Non binary data that is less then 30001 or greater then 40001.
  3. Devices states it is J-Bus.
  4. Register address is displayed in Hexadecimal format.

Hints to use Fixed Address Blocks

  1. Any address register above 30000 or 40000, unless it claims to be a JBus device.

If it is still unclear which addressing format to use then experiment with read only data and value pages in the Xenta Servers. Pick a point that you can easily confirm the value, add both address formats to a device template, and then confirm the proper format with a values page. Once you know how to read one point the rest of the product documentation is easier to work with.

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4058
  • PeterLarsen22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of