Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Modbus Xdriver Enabled Commport - RTU or TCP/IP?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Modbus Xdriver Enabled Commport - RTU or TCP/IP?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2246 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Modbus Xdriver Enabled Commport - RTU or TCP/IP?

Picard Product_Support
‎2018-09-10 01:23 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:53 AM

Issue

Distinguishing whether an xDriver-enabled commport on a controller is set for Modbus RTU or Modbus TCP/IP.

Environment

CX9900, CX9940

CX9680

bCX4040

Cause

How does one know if the xDriver-enabled commport on a controller is for Modbus RTU or Modbus TCP/IP?

Resolution

Open the controller editor and go to the Options tab.

At a minimum the Modbus RTU XDriver, like all Xdrivers, requires Bit 0 for the commport be Xdriver enabled. The most common example would look like this:

Xdrvr Commx: 00000001(####).

In the above example x = commport number.

The four digit number in parentheses indicates whether an Xdriver file is loaded into the port. If it is 0000 then no Xdriver file is loaded into the port. A number such as 4767 corresponds to "Xdriver Valid" line at the end xdriver XDR file. You can edit the XDR file with a text editor and go to the bottom to see this.

 

In addition to Bit 0 being enabled for the commport, the Modbus TCP/IP Xdriver requires Bit 3 to be Xdriver enabled.  A common example of this would look like this:

Xdrvr Commx: 00000009(####).

The 00000009 is in hexadecimal format -  converting this to an 8-bit binary number you get 00001001. The furthest right bit is Bit 0 and the 4th from the right is Bit 3. Both are set to 1 which means they are Xdriver enabled. For a further explanation see page 15 of the linked Modbus TCP/IP Xdriver User Guide.  

Note: Since Bit 0 is enabled in both of the above examples, the Modbus RTU Xdriver will work on either. But only the second example will load the Modbus TCP/IP Xdriver.  

 


 

Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (1)
  • Find more articles tagged with:
  • 5878
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore