Issue
ModBMS will not allow an OPC Client to write OPC DA values to Sigma. But, reading the ModBMS/Sigma values does work.
Environment
Sigma 4.04 and below
ModBMS
OPC Client
Cause
ModBMS uses the DDE functions to read/write data to the Sigma server. A Sigma release 4.04 and below the write function was not supported and was fixed in Sigma release 4.05 onwards.
Resolution
Upgrade to Sigma 4.05 (onwards) where the DDE write function has been fixed.