Issue
ModBMS not connecting to Sigma, error " Not monitoring, DDE not init "
Product Line
Satchwell Sigma
Environment
- Sigma
- ModBMS
Cause
Windows 7 and Server 2008 removed a functionality that allowed ModBMS to be able to poll the Sigma server.
Resolution
- A Sigma executable file is required to be running in the background.
- Create a shortcut to the desktop and open c:\Sigma\Bin\SigTop.exe.
- ModBMS will now poll the Sigma server and the error disappears.