Issue
ModBMS does not allow an OPC Client to write OPC DA values to Sigma. However, reading values from ModBMS/Sigma is successful.
Product Line
Satchwell BAS & SigmaEnvironment
- Sigma versions 4.04 and earlier
- ModBMS
- OPC Client
Cause
ModBMS uses DDE (Dynamic Data Exchange) functions to read and write data to the Sigma server.
In Sigma versions prior to 4.05, the DDE write function was not supported. This limitation was resolved in Sigma version 4.05 and later.
Resolution
To enable OPC DA write functionality, upgrade Sigma to version 4.05 or later, where the DDE write capability has been implemented.