Issue
The enhanced logging module in the MicroNet 50 Series does not continue logging once full, unless explicitly configured to do so.
Product Line
Satchwell MicroNet
Environment
- Satchwell MicroNet
- MN X50 Series controllers
Cause
In MicroNet 100 Series controllers, the logging object was designed to automatically overwrite the oldest values when the log was full.
However, the MicroNet 50 Series logging object requires additional configuration to replicate this behavior.
Resolution
⚠️ Important Notices
- The MicroNet 50 series controllers (MN350, MN450, MN550, MN650 LCD and Touchscreen) have been withdrawn from sale.
- The IAC 420, IAC 600, and Touchscreen models have also been discontinued.
- No direct replacements are currently offered.
For more details, refer to:
- PA-00495 - Notice of Withdrawal - Satchwell Sigma (PDF)
- PA-00528 - End of Commercialization - Satchwell Sigma (PDF)
Logging Object Configuration
Legacy Behavior (100 Series & IAC)
- The default configuration allowed logs to overwrite older entries automatically.
- Example configuration:
MicroNet 50 Series Behavior
- To replicate legacy behavior, you must configure external nodes of the logging object.
- Example configuration:
Additional Resources
For detailed configuration guidance, refer to the following documents:
-
VisiSat V1.2 Engineering Guide
(Covers IAC 400, IAC 420, IAC 600, and Touchscreen) -
VisiSat V2.1 Engineering Guide
(Covers MN300, MN440, MN500, MN620, MN350, MN450, MN550, MN650, MNLCD, and MN Touchscreens)