Meter Points, Pulse Points Frequency, and Pulse Point Width Configuration
  • Meter Points, Pulse Points Frequency, and Pulse Point Width Configuration
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
‎2018-09-06 01:15 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-20 05:44 PM
Understanding the maximum pulse repetition rate and minimum pulse width for pulse/meter points configured on digital inputs. Also, identifying where pulse points can be configured on x96 controllers.
Satchwell BAS & Sigma
  • BAS or Sigma Controllers: UNC532, UNC632, UNCx96
  • Digital Input Modules (e.g., S-UNC-DI)
Clarification needed on configuration limits and locations for pulse/meter points in various controller models.
UNC532
  • Channels: 1–2
  • Object Numbers: 81–82
  • Repetition Rate: 10 Hz
  • Minimum Pulse Width: 50 ms
  • Note: Channels 3–10 (Object Nos. 83–90) configured as pulse objects have a reduced repetition rate of 0.5 Hz
UNC632
  • Channels: 1–10
  • Object Numbers: 81–90
UNCx96 (with S-UNC-DI module)
  • Channels: 1–16
  • Object Numbers: 81–96
  • Important: Pulse objects can only be configured in slot 6 of the controller.
  • Satchwell BAS & Sigma
Tags (2)
  • 6257
  • CraigEllis25