Issue
Guidance on merging index files from two separate Sigma sites into a single unified site.
Product Line
Satchwell BAS & SigmaEnvironment
Sigma - all releases.
Cause
When consolidating two Sigma systems, it's necessary to merge their respective index files (index.rec and index.bin) without duplicating controller numbers or introducing system errors.
Resolution
Pre-Merge Preparation
-
Backup
- Always create backup copies of both site index files before proceeding.
-
Error Check
- Use SigmaX > Doctor Error Check on both site indexes
.
- Ensure both sites are free of “A” errors.
- Save or print the error reports for documentation.
- Use SigmaX > Doctor Error Check on both site indexes
Merge Procedure
-
Directory Setup
- In SigmaX > Sigma Utilities > Merge Index Files, use the default directories or create your own:
Master Indexdirectory → for the main site index filesSecondary Indexdirectory → for the new site index files
- In SigmaX > Sigma Utilities > Merge Index Files, use the default directories or create your own:
-
File Placement
- Place the respective
index.recandindex.binfiles into the appropriate directories.
- Place the respective
-
Merge Execution
- Click “Merge Index” to initiate the process
.
- Click “Merge Index” to initiate the process
-
Post-Merge File Handling
- Copy the newly created index files from the output directory to
C:\Sigma\Data. - Also copy all controllers from both sites into
C:\Sigma\Data.
- Copy the newly created index files from the output directory to
-
Validation
- Perform a visual check of the merged index structure.
- Run another Doctor Error Check to confirm the final index is error-free
.
- Save or print the final error report.
-
Index Conversion
- In SigmaX > BasConv
:
- Set Start Release to Sigma 2
- Set End Release to Sigma 4
- Check the “Index File” box
- Click “Convert” to generate
IndexEx.rec
- In SigmaX > BasConv
Important Notes
- This article focuses solely on merging index files.
- Additional components such as:
- Controller operating files
- Route sets
- Access classes
- Graphics
- Must be handled separately when combining two sites.