Issue
Product Line
TAC IA SeriesEnvironment
I/A Series R2 UNC
Cause
Resolution
- The recommended maximum number of Modbus TCP connections is 24 for JACE-4 (UNC-410) and JACE-5 (UNC-510/UNC-520).
- Default setting for
maximumConnectionsis 1. - If multiple Master TCP devices need simultaneous access to the station as a Modbus slave, increase
maximumConnectionsaccordingly. - Important: Each Modbus TCP device or gateway shadowed in the station consumes a separate processing thread. Exceeding the recommended limit may impact performance.