Maximum TCP Connections for I/A Series R2 UNC with Modbus TCP Driver
  • Maximum TCP Connections for I/A Series R2 UNC with Modbus TCP Driver
  • CraigEl
    CraigEl
  • WaynePeters
    WaynePeters
‎2018-09-06 01:15 PM
Last Updated: Administrator CraigEl Administrator ‎2025-12-11 04:19 PM
What is the maximum number of TCP connections supported on an I/A Series R2 UNC running a Modbus TCP driver?
TAC IA Series
I/A Series R2 UNC
The system needs to support multiple Modbus TCP devices or gateways simultaneously. Each device or gateway uses a separate processing thread, and the platform has a finite number of threads available.
  • The recommended maximum number of Modbus TCP connections is 24 for JACE-4 (UNC-410) and JACE-5 (UNC-510/UNC-520).
  • Default setting for maximumConnections is 1.
  • If multiple Master TCP devices need simultaneous access to the station as a Modbus slave, increase maximumConnections accordingly.
  • Important: Each Modbus TCP device or gateway shadowed in the station consumes a separate processing thread. Exceeding the recommended limit may impact performance.
  • TAC IA Series
Tags (2)
  • 6262
  • CraigEllis25