Issue
Can a supervised input be mapped from a b3 and/or an i2 controller up to a
numeric in a BCX?
Environment
i2
b3
bCX
Cause
A project will require some supervised inputs on b3 and/or i2 controllers. Can these points be mapped to a bCX?
Resolution
Be aware that only certain b3 and i2 controllers support the supervised input type.
Supervised inputs on these controllers can be mapped via a Plain English program to an InfinityNumeric in a bCX (or other applicable network level controllers).
On a v1.93 system with a bcx9640 we mapped a supervised input on an i2800. The InfinityNumeric editor displayed all three supervised states: On, Off, and Trouble.