Issue
manualCmd field exists in objects such as LcmAnalogCmd, LcmBinaryCmd, GcmAnalogCmd, and GcmBinaryCmd, but the option does not appear.Product Line
TAC IA SeriesEnvironment
Niagara R2 system with Network 8000 GCM/LCM integration
Cause
manualCmd option from being available until the object is linked to an appropriate output object.Resolution
To enable manual commands:
- Connect the command object (
AnalogCmdorBinaryCmd) to an Analog Output or Binary Object. - Issue a change using the connected output object.
- After this step, the option to issue a manual command to the
AnalogCmdorBinaryCmdobject will become available.