MN50-LCD changes the displayed value to zero when connected to a 100 series controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MN50-LCD changes the displayed value to zero when connected to a 100 series controller.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Gary
    Gary
  • Product_Support
    Product_Support
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • sesa119747
    sesa119747

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1725 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MN50-LCD changes the displayed value to zero when connected to a 100 series controller.

Picard Product_Support
‎2018-09-11 03:57 AM

Issue

The 50 series version of the LCD unit can fail to re-poll analogue values when used in conjunction with an old series MN controller, this will only occur after the controller has been power cycled. This problem does not apply to the 50 series controller range.
 

Product Line

 Satchwell Sigma

Environment

MicroNet 50 series LCD connected to 100 series controller.

Cause

With older controllers, although the initial poll from the LCD brings back the controller analogue values, the LCD changes the displayed value to zero. This issue does not affect digital state displays or the analogue values contained within the controller’s scheme.

Resolution

A temporary workaround is to ensure the controller is not power cycled after its configuration has been downloaded.
Firmware version MNLCD5W is now available for correcting this issue.
If you require updated firmware for your MN50-LCD or MN50-LCDP units. Please contact the Product Support Services department.
Specification numbers affected:

  • MN50-LCD  (Firmware version MNLCD5V)
  • MN50-LCDP  (Firmware version MNLCD5V)

This issue will only affect the MN50-LCD or MN50-LCDP when used with the

  • MNN-30-100
  • MNN-44-100
  • MNN-50-100
  • MNN-62-100
  • Liberty (All variants)

This problem does not apply to the 50 series controller range.

Firmware version MNLCD5W is available from Product Support
By supplying the site name, and the number of MN50-LCD firmware EEPROMs required. 
 

Procedure to change the MN50-LCD firmware.

  1. Observe standard electrostatic precautions.
  2. Power the MN50-LCD/P and MicroNet 100 series controller down.
  3. If MN50-LCD remove the LCD from the controller and unplug the ribbon cable.
  4. If MN50-LCDP remove the power/communications plug from the LCDP, then remove the back cover.
  5. Remove the MN50-LCD/p's firmware EEPROM from IC13 socket. (Highlighted in the below image in blue)
  6. Carefully line up the legs of the new EEPROM with the socket.
  7. Press the new MNLCD5W firmware EEPROM into the socket.
  8. Restore the power to the controller
  9. Download the controller and LCD program to the controller.
  10. Restore the power and plug the MN50-LCD/P into the controller and allow it to upload is configuration.
  11. Check all analogue readings are now reading satisfactorily.

Updated June 2019
The MicroNet 50 series range MN350, 450, 550, 650 LCD and Touchscreen have been withdrawn from sale.
The IAC 420, 600 and Touchscreen have now also been withdrawn from sale.
No direct replacement is offered.
Further information on these changes can be found in PA-00495 and PA-00528 

A limited number of MNLCD5W firmware EEPROMs are available.

Labels (1)
Labels:
  • Satchwell MicroNet
Tags (1)
  • Find more articles tagged with:
  • 12564
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of