Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Loss of resolution on metering points when the number is 7 digits or longer

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Loss of resolution on metering points when the number is 7 digits or longer
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Dave_Shore
    Dave_Shore
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1942 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Loss of resolution on metering points when the number is 7 digits or longer

Picard Product_Support
‎2018-09-06 02:03 PM

Issue

When working with numbers that are 7 digits or longer the number is displayed in exponential format and there is a loss resolution in the lower digits that can cause an issue with metering applications. This can be an issue when using pulse counter inputs.

Product Line

Andover Continuum

Environment

All Continuum controllers and modules that support Pulse counting with Counter inputs

Cause

The number formatting throughout the Continuum product is 32 bit IEEE Floating point notation, for numbers up to 7 digits long they will be displayed as a regular decimal number, for larger numbers they will be displayed in exponential format:

Significant digits × baseexponent

This allows Continuum to work with huge numbers like 123.45 x 1067 but has the disadvantage that as the numbers get larger there will be a loss of resolution in the lower digits starting with the units.

Resolution

When working with pulsed inputs from meters try to keep the size of the numbers down, putting scaling factors of x10 and x100 only makes the numbers bigger, so where possible scale the numbers down and upscale the units.

For example when scaling an input where you would enter a conversion of: Value+(ElecValue * 10)

Instead use: Value+(ElecValue*0.1) and change the units to Kilo Units, Mega Units etc.

If you have to measure large pulsed numbers another option is to split the large numbers across 2 Numerics, so in Plain English when a value gets to 999,999 then add 1 more pulse, you get 1 in the upper number and 0 the lower number. This can then be displayed on a graphic with 2 adjacent text boxes.

Where very accurate metering is required the best solution is to use meters with an intelligent data interface that supports one of the common open protocols supported by Continuum (i.e. BACnet MS/TP, Modbus or M-Bus via X Drivers). This solution means there is no chance of missing a pulse or Continuum getting out of sync' with the meter.

Note: If you need to set the lower number back to zero, then the object first needs to be disabled. If this is a BACnet bCX then the BACnet name (eg BACnetDevices\bCX25\Counter2) needs to be used within the PE Program

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4741
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore