Issue
Lookup table for the AIC Analogue Input Configuration for different sensors.
What types of sensors can be used with the MPM controller?
Product Line
EcoStruxure Building Expert
Environment
- Multi Purpose Manager
- AIC
Cause
A lookup table is required for a sensor that is not listed in the AICs.
What sensors can be used?
Resolution
For the Satchwell range (new generation or T range) STP660, STC600, STR600 series. Note the engineering output is Celsius.
For the TAC range STP100 series, STC100, STR100 series, STD100 series. Note the engineering units is Celsius.
For the Andover range STP500 series, STC500, STR500 series, STD500 series. Note the engineering units is Celsius.
AIC 1 to AIC 10 are empty Analogue Input Configurations, the remainder are pre-configured as below.
For 10K Type II in Celsius use AIC 11
For 10K Type II in Fahrenheit use AIC 12
For 10K Type III in Celsius use AIC 13
For 10K Type III in Fahrenheit use AIC 14
For 1K PT1000 RTD Platinum in Celsius use AIC 15
For 1K PT1000 RTD Platinum in Fahrenheit use AIC 16
For 1K PT100 RTD Platinum in Celsius use AIC 17
For 1K PT100 RTD Platinum in Fahrenheit use AIC 18
For 1K NI1000 RTD Nickel in Celsius use AIC 19
For 1K NI1000 RTD Nickel in Fahrenheit use AIC 20