Lookup table for the AIC Analogue Input Configuration for different sensors. What types of sensors can be used with the MPM controller?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Lookup table for the AIC Analogue Input Configuration for different sensors. What types of sensors can be used with the MPM c...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2363 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Lookup table for the AIC Analogue Input Configuration for different sensors. What types of sensors can be used with the MPM controller?

Picard Product_Support
‎2018-09-11 08:17 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:05 AM

Issue

Lookup table for the AIC Analogue Input Configuration for different sensors.

What types of sensors can be used with the MPM controller?

Product Line

EcoStruxure Building Expert

Environment

  • Multi Purpose Manager
  • AIC

Cause

A lookup table is required for a sensor that is not listed in the AICs.

What sensors can be used?

Resolution

For the Satchwell range (new generation or T range) STP660, STC600, STR600 series. Note the engineering output is Celsius.

 

For the TAC range STP100 series, STC100, STR100 series, STD100 series. Note the engineering units is Celsius.

 

For the Andover range STP500 series, STC500, STR500 series, STD500 series. Note the engineering units is Celsius.

 

AIC 1 to AIC 10 are empty Analogue Input Configurations, the remainder are pre-configured as below.

For 10K Type II in Celsius use AIC 11

For 10K Type II in Fahrenheit use AIC 12

For 10K Type III in Celsius use AIC 13

For 10K Type III in Fahrenheit use AIC 14

For 1K PT1000 RTD Platinum in Celsius use AIC 15

For 1K PT1000 RTD Platinum in Fahrenheit use AIC 16

For 1K PT100 RTD Platinum in Celsius use AIC 17

For 1K PT100 RTD Platinum in Fahrenheit use AIC 18

For 1K NI1000 RTD Nickel in Celsius use AIC 19

For 1K NI1000 RTD Nickel in Fahrenheit use AIC 20

Labels (2)
Labels:
  • EcoStruxure Building Expert
  • Field Devices
Attachments
Satchwell.zip
TAC 1.8k.zip
Andover.zip
Tags (2)
  • Find more articles tagged with:
  • 14697
  • DavidChild21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore