Logon failures with WebReports

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Logon failures with WebReports
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1677 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Logon failures with WebReports

Picard Product_Support
‎2018-09-11 01:05 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-02-17 03:23 PM

Issue

  1. Data not passing from Enterprise Server to Reports Server after upgrading to 1.6
  2. Reports folder does not appear on new 1.6 Reports installations
  3. Logon failed at attempt no. XX User account has been temporarily disabled. Contact your administrator.

Product Line

EcoStruxure Building Operation

Environment

Building Operation WebReports 1.6 and above

Cause

New features require additional configuration to allow Reports to function. Specifically, the Reports installation requires that the SystemReportsService user account be enabled before installation.  If this is not done, the steps below must be taken.

 

For Issue #3:

If the user account used to access WebReports is changed through WorkStation, WebReports is still using the previous account password to access the Enterprise Server, this will lock the user account out and if used to log in to WorkStation will indicate that the account is disabled

To verify that this is what is causing the lockout, open the Report Agent log StruxureWareReportingAgentLog and check for Logon Failed at attempt xx Reason: User account temporarily disabled.... error is shown.

The default path for this log file is:

C:\Program Files (x86)\Schneider Electric (StruxureWare)EcoStruxure\Building Operation

Resolution

During the installation of WebReports, you will see the popup message below. In order for the installation to work correctly, the SystemReportsService account must be changed to enabled before clicking OK.

Ensure that SystemReportsService user account is enabled in the Enterprise Server before you proceed with the installation process further.

To correct this error after installation:

  1. If running stop the Repot Agent Service and wait 1 minute before proceeding
  2. Log into Workstation using the admin account
  3. Modify the user "SystemReportsService" (or user account used) that is part of the Local domain
  4. Check/Change the property "Disabled" is set to "False
  5. Change/verify the password
  6. Close WorkStation
  7. On the Report Server open the program "Building Operation WebReports Administrator"
    WebReports-Administrator.png
  8. Enter the newly created password for the SystemReportsService (or account used)
  9. Click Apply - a successful update should be reported.
  10. Click Save
  11. Close Building Operation WebReports Administrator
  12. Restart the Reporting Agent Service.
  13. Verify logins now work.

For additional Authentication issues please see the online help topic: Authentication Failed (se.com)

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 17464
  • RobertAndriolo22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of