Issue
A site is converted from TAC Vista to EcoStruxure Building Operation using TAC Vista Conversion Tool and all TGML graphics work fine.
After a TGML graphic is edited all links or binding paths in the graphic are changed.
Example:
Before
After
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Workstation
- TAC Vista Conversion Tool version 2.X
Cause
This issue will only be seen in TGML graphics which originally have been OGC graphics in TAC Vista and then converted to TGML graphics at some point.
Resolution
This issue is fixed in TAC Vista Conversion Tool version 3.02 and later.
Redo the conversion using a version of the TAC Vista Conversion Tool 3.02 or later.