Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

LON communications throttling in MNL-800 controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LON communications throttling in MNL-800 controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2257 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LON communications throttling in MNL-800 controllers

Picard Product_Support
‎2018-09-06 02:39 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-09-08 11:22 AM

Issue

Too much LON communications traffic can cause LON communications errors.

Product Line

TAC IA Series, EcoStruxure Building Operation

Environment

  • I/A Series MNL 800
  • Building Operation Automation Server Premium LON Network 
  • I/A Series R2, AX, N4 Jace LON Network

Cause

Sending output LON SNVT values too frequently or more often than reasonably needed.

Resolution

There are a series of NCI (configuration) objects that control the transmission and reception of these data values on the LON network.
One of four NCI objects (nciSndHeartBeatA, B, C, or D) is assigned to each NVO object in the application program. This value regulates the periodic LON transmission queuing of the NVO object values for each binding.
One of four NCI  objects (nciRcvHeartBeatA, B, C, or D) is assigned to each NVI object in the application program. This value regulates the fallback timeout for each NVI object value. If a value is not received via the binding in this time period, the NVI object value will revert to its application-defined default value.

In an MNL-800 controller, there are two additional NCI objects that are used to regulate the flow of data onto the LON network.
The nciMinOutTime object is used to throttle the transmission of all data values queued to be sent via bindings over the LON network. This NCI object sets the transmission time interval between each NVO value being sent on the network. The important fact here is that the product of the number of bound NVO values times this interval (nciMinOutTime) must be LESS than the shortest nciSndHeartBeatX (X=A, B, C or D) interval.

For example, if the Send HeartBeat is set to the default of 120 seconds and there are 60 NVO SNVTs bound from this controller, the nciMinOutTime must be set to a value of fewer than 2 seconds.  The recommendation for setting this SNVT value one half the shortest nciSntHrtBr divided by the number of NVO SNVTs bound from the controller.  

The nciMinPropTm object is used to regulate the transmission queuing of changing bound NVO object values. This timer acts as a time-based filter to prevent a rapidly changing NVO value, such as a constantly changing temperature, from overwhelming the communication capacity of the LON network. Typically this value is set to a value of 1 to 5 seconds.

Additional information can be found in Chapter 6 of the WorkPlace Tech Tool 4.0 Engineering Guide (F-27254).

BACKGROUND:
This section is provided to give the reader a basic understanding of bound LON communications, as applied to LON controllers in general.
Data communications across a LON network is accomplished by using a LON Network management tool to create a binding between a device with a data source (NVO object) and one or more devices with data receivers (NVI objects) in other LON controllers. The device containing the data source will send the bound data value at a periodic rate, as defined by the associated SendHeartBeat NCI object, and whenever the value of that object changes. If the NVI object does not receive a value from the sender (bound NVO object) within a specified time period, as defined by the associated ReceiveHeartBeat NCI object, the NVI object will use a local fallback value until such time as it receives a new value via the binding.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 3366
  • RandyDavis22
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of